D

Dave-Titan

just got the call . . . . i passed C&G 2391 course!

did everyone find out today?
 
TL;DR
C&G 2391 course
Last edited by a moderator:
Hello Mate,
I just got my results and i have passed.I will be honest I have been out the game for a while.Thought i would dust down the tools and get back involved.
I studied like a mad man for a month.
It is all about study and getting the book into your head get load of past papers in you and you will be fine.

Good Luck
Well done that man:)
 
Upvote 0
Only as hard as you want it to be, i read too much into "2391 rock hard etc..." , but asi started doing past papers i was questioning my own ability because i thought " this isnt as hard as people make out OR am i just been stupid and ended up thinking the answer was incorrect

Beleve in yourself mate, i didnt and its been on my mind for 2 months now waiting for the result luckily i found out today i passed :), its a shame that you dont get a percentage
 
Upvote 0
And well done to you too Vernam :)
I reckon (after the event) a lot comes down to exam nerves but if you're well prepared you should be ok.
Just like any other exam really
 
Upvote 0
regarding volts drop

i have an equation of

mv x ib x l / 1000

so what is the equation

(r1 + rn) x cf x ib
answer x 100 / 230

will somebody please clear this up
 
Upvote 0
Voltage = Current x Resistance (V = I x R)

r1 + rn is the resistance of your circuit at 20°C.

cf is the correction factor for conductor operating temperature. As resistance increases with temperature you need to adjust it for 70°C. You do this by multiplying your measured resistance by 1.2

You then multiply the new value by your design current which gives you the voltage drop on the circuit at 70°C.
 
Upvote 0
Both. It's up to you. They will both give you the same result.

The mV/A/m values from your first equation are calculated using the other equation.

mV/A/m = (r"1 + r"n) x 1.2 where r"1 = resistance per meter of line conductor and r"n = resistance per meter of neutral conductor.

So in the case of 2.5mm² you would get...

r"1 = 7.41mΩ per meter
r"n = 7.41mΩ per meter
r"1 + r"n = 14.82mΩ per meter
(r"1 + r"n) x 1.2 = 17.78 mΩ per meter (rounded up to 18) which is the value in BS 7671
 
Upvote 0