You can work out what the PFC should be when tested single phase given the information.No I don’t know tbh can you help with this question please?
The key here is calculating your pfc for the three phase and single phase because two boards are single phase and the other two three phase. Then as in #6 which ones then need checking.
the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?You can work out what the PFC should be when tested single phase given the information.
You can then convert that to 3 Phase PFC.
With that information think about which DB protective devices short circuit breaking capacity might need checking.
This is a periodic Inspection and test, when you test on a Periodic a test result might give you reasons to perform further tests and this is what the question is probing.the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?