During Periodic Inspection and Testing, prospective fault current has been tested at the main distribution board (Main DB) using a single-phase test instrument.

The supply and installation form part of a 400 V three-phase TN-C-S system. The value of Zₛ (earth fault loop impedance) for this installation is 0.05 Ω.

Information about the protective devices installed at the remote distribution boards (DBs) is as follows:

Main DB: 3 phases, 10 kA
DB1: 3 phases, 7.5 kA
DB2: 3 phases, 7.5 kA
DB3: 1 phase, 7.5 kA
DB4: 1 phase, 6 kA

At which points in the installation must further testing be carried out?

a) DB1 and DB2
b) DB3 and DB4
c) DB1, DB2 and DB3
d) DB1, DB2 and DB4
 
Upvote 0
The key here is calculating your pfc for the three phase and single phase because two boards are single phase and the other two three phase. Then as in #6 which ones then need checking.
 
Upvote 0
The key here is calculating your pfc for the three phase and single phase because two boards are single phase and the other two three phase. Then as in #6 which ones then need checking.



Further testing should be carried out at DB1, DB2, and DB4 to confirm that the PFC at these points does not exceed the breaking capacities of their respective protective devices is to hid correct ?
 
Upvote 0
You can work out what the PFC should be when tested single phase given the information.

You can then convert that to 3 Phase PFC.

With that information think about which DB protective devices short circuit breaking capacity might need checking.
the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?
 
Upvote 0
the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?
This is a periodic Inspection and test, when you test on a Periodic a test result might give you reasons to perform further tests and this is what the question is probing.

Think about PFC and what it cannot be at points further from the origin?

Given the above info why the single phase ones when we know the maximum single phase PFC at the origin?

Why the 3 phase ones?
 
Upvote 0
I encountered a very confusing question in the 2391 online exam.
What is recorded in the schedule of inspections for the new shower circuit?
a.N/A
b.N/v
c.LIM
d.FI

what is the answer for that
 
Upvote 0
Ask yourself which ones would not be recorded remember this is for an Electrical Installation Certificate, three of those would definitely not be suitable for the Certificate.
 
Upvote 0
Hi folks, I managed the 2391 computer based exam the other day :innocent: , next it's the practical day. What can/should I take with me? I assume ...
  • books (regs/GN3/OSG),
  • MFT+cert,
  • voltage stick+proving unit,
  • lock-off kit,
  • hand tools
  • R1+R2 test links
Anything else, what about wander lead?

Does my volts stick need a calibration cert?

Any help much appreciated :D
 